消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电房一定需要安装防火门吗

我们单位是工贸企业,配电房是单独建筑,而且是单层建筑,目前安装的是钢门,消防检查中要求我们更换成防火门,查了相关规范,也不知道哪个规范强制要求配电房需要安装防火门,求大神告知一二

每日一学 | 2024-09-24 07:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 10

磊中 2024-09-24 09:14 10 [回复]举报

配电房是单独的建筑,等于直接开向室外的门了,那是可以不用防火门的哦

根据建筑防火通用规范6.4.3 除建筑直通室外和屋面的门可采用普通门外,

安洪全 2024-09-24 09:16 20 [回复]举报

花生12138 2024-09-24 09:54 00 [回复]举报

单独建筑不用,配电房门开向建筑内才需要防火门

三废工程师 2024-09-24 09:57 00 [回复]举报

直通室外的门,不需要

周家斌 2024-09-24 10:32 10 [回复]举报

1、一般情况下直通室外的门可以为普通门,二般情况除外!(与相邻建筑的关系)

2、当地的供电部门有要求为防火门的,(我所在的城市供电部门就要求是防火门,不管是建筑内的还是独立建造的配电房都要求是防火门)

无糖可乐 2024-09-24 16:54 00 [回复]举报

GB50016-2014(2018年版):GB55037只是废除了该条的强条属性,条文没有废除。

一只小锦Li 2024-09-25 08:13 10 [回复]举报

我看了别的人给的评论,大多数都考虑问题单一,首先直通建筑外的门可以用普通门,但有个问题,需要考虑到此处房间性质,配电房严格来说应该算是重要设备房吧,归属于消防安全重点部位,应采用防火门,从严原则的话要防火们的

zkp128 2024-09-25 11:33 20 [回复]举报

如果该配电房是变配电房,要执行 20kV及以下变电所设计规范 GB50053-2013第6.1.3条6款“6 变电所直接通向室外的门应为丙级防火门。”

阳明心   回复: zkp1282024-09-28 13:08

对的,应该区别变电房还是配电房

0    0 [回复]举报

jinyanwu 2024-11-29 11:49 00 [回复]举报

你参考一下这个,《民用建筑设计统一标准 GB50352-2019》

先确定一下是什么性质的场所。

关闭

关闭

手机APP下载