消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵出水管压力表在泵正常运行时压力值是0正常吗?如果不正常,应该是多少

消防水泵出水管压力表在泵正常运行时压力值是0正常吗?如果不正常,应该是多少

柠檬不萌 | 2024-09-19 15:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

阳明心 2024-09-20 08:38 00 [回复]举报

不正常,具体应该多少看设计

柠檬不萌   回复: 阳明心2024-09-29 14:53

水泵是补水泵,从河里给消防水池补水的,设的抗震压力表,就泵启动的瞬间压力表会到0.1左右,然后就回0位了

0    0 [回复]举报

阿龙 2024-09-20 11:38 00 [回复]举报

检查一下压力表前阀门是不是关了,或者压力表是不是坏了,正常情况下你水泵不启动出水管网都是有压力的,消防水泵出水管网是连通报警阀下腔或者直接连接消火栓管网的,不可能没有压力。

柠檬不萌   回复: 阿龙2024-09-29 14:54

水泵是补水泵,从河里给消防水池补水的,设的抗震压力表,就泵启动的瞬间压力表会到0.1左右,然后就回0位了

0    0 [回复]举报

磊中 2024-09-24 16:19 00 [回复]举报

肯定是不正常的,如果是泵正常运行而没有出水的设备,那这个时候出水管上的压力是最大的,但是这个压力也不能大于设计压力的140%,当出流量为设计流量的150%时,其出口压力不应低于设计工作压力的65%

柠檬不萌   回复: 磊中2024-09-29 14:54

水泵是补水泵,从河里给消防水池补水的,设的抗震压力表,就泵启动的瞬间压力表会到0.1左右,然后就回0位了

0    0 [回复]举报

磊中   回复: 柠檬不萌2024-10-08 16:40

只要有水经过就会产生压力的,如果量程太大,最小值也就是说精确值也过大那可能显示不了那么小的值,比如0.01MPa。他就显示是0往上一点点和0差不多,不过只要管内有水就一定会产生压力的,一般情况下这个压力和水泵的扬程是相符的

0    0 [回复]举报

关闭

关闭

手机APP下载