中庭扶梯 不是默认不得作为疏散的吗,为何 卷帘边还设置温感?














中庭扶梯口 这设置温,烟,是2步降还是1步降, 还是说不管温,烟,就是1步降?? 为什么要设置温,   给设计思路 整蒙了。



知耻也要问 | 2024-11-05 08:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

jinyanwu 2024-11-20 16:31 00 [回复]举报

设置温感和烟感你可以这样理解,当没有温度和烟气过来时,虽然有报警信号,但这个地方还是可以作为疏散一个口使用的,当温感或烟感其中之一动作了,那就可能会执行两步降,第一步1.8米,第二步降到底。一般都是一烟一温,比较牢靠;温感还有一个作用,说明火烧过来了,应该会启动消防泵,当然这个需要看消防设计文件。