哪些场所需要安装电气火灾监控、消防电源监控?

哪些场所需要安装电气火灾监控、消防电源监控,有没有相关规范条文要求

阿宸宸宸宸OK | 2024-08-27 08:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

陈泽平 2024-08-27 08:47 30 [回复]举报

10.2.7 老年人照料设施的非消防用电负荷应设置电气火灾监控系统。下列建筑或场所的非消防用电负荷宜设置电气火灾监控系统:
      1 建筑高度大于50m的乙、丙类厂房和丙类仓库,室外消防用水量大于30L/s的厂房(仓库);
      2 一类高层民用建筑;
      3 座位数超过1500个的电影院、剧场,座位数超过3000个的体育馆,任一层建筑面积大于3000m²的商店和展览建筑,省(市)级及以上的广播电视、电信和财贸金融建筑,室外消防用水量大于25L/s的其他公共建筑;
      4 国家级文物保护单位的重点砖木或木结构的古建筑。


13.3.8 设有消防控制室的建筑物应设置消防电源监控系统,其设置应符合下列要求:

    1 消防电源监控器应设置在消防控制室内,用于监控消防电源的工作状态,故障时发出报警信号。
    2 消防设备电源监控点宜设置在下列部位:
    1)变电所消防设备主电源、备用电源专用母排或消防电源柜内母排;
    2)为重要消防设备如消防控制室、消防泵、消防电梯、防排烟风机、非集中控制型应急照明、防火卷帘门等供电的双电源切换开关的出线端;
    3)无巡检功能的EPS应急电源装置的输出端;
    4)为无巡检功能的消防联动设备供电的直流24V电源的出线端。

张治福 2024-08-28 08:29 00 [回复]举报

现实工程中,施工不规范,系统很鸡肋,误报不断,不好用。这类产品在电气行业中,实属成熟产品,在消防行业上应用就问题多多。