消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于线型感温探测器的设置要求

各位老师,请问变压器、油箱、柴油发电机等设置缆式感温火灾探测器时要设置2路(1路短路报警,2路短路联动灭火),这个是在哪部规范有要求?只设置1路可以吗?

消防小萌新 | 2024-05-09 23:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

蜗牛仔仔 2024-05-10 11:07 00 [回复]举报

水喷雾灭火系统技术规范 GB50219-2014 >

6.0.6 分段保护输送机皮带的系统,在启动起火区段的雨淋报警阀的同时,应能启动起火区段下游相邻区段的雨淋报警阀,并应能同时切断皮带输送机的电源。
6.0.7 当自动水喷雾灭火系统误动作会对保护对象造成不利影响时,应采用两个独立火灾探测器的报警信号进行联锁控制;当保护油浸电力变压器的水喷雾灭火系统采用两路相同的火灾探测器时,系统宜采用火灾探测器的报警信号和变压器的断路器信号进行联锁控制

关闭

关闭

手机APP下载