自动喷水系统是否可以与消火栓系统共用水泵。

自动喷水系统没有设置水泵,是否可以接入消火栓系统,用消火栓系统的水泵?

@小白 | 2024-04-24 14:03
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

灭邪斩 2024-05-04 18:40 00 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014

       8.1.7 室内消火栓给水管网宜与自动喷水等其他水灭火系统的管网分开设置;当合用消防泵时,供水管路沿水流方向应在报警阀前分开设置。

      两个系统可以合用消防泵,但应符合规范要求,不能相互影响各自系统灭火功能。

    


南明离火 2024-05-05 10:39 00 [回复]举报

宜设置独立的,但是特殊情况  也见过共用的