单位因经营不善,关停了,所有消防设施停用,需要与当地的消防救援机构进行备案吗?

lmsunny | 2024-04-18 17:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2024-04-19 08:58 00 [回复]举报

停用影不影响其他单位的消防设施使用?如果不影响,其实报不报的也无所谓,但如果是消防安全重点单位的话,必须报。

消防网友68723 2024-04-19 10:00 10 [回复]举报

消防设施通用规范 GB55036,2.0.9 消防设施投入使用后,应定期进行巡查、检查和维护,并应保证其处于正常运行或工作状态,不应擅自关停、拆改或移动。超过有效期的灭火介质、消防设施或经检验不符合继续使用要求的管道、组件和压力容器不应使用。

龙蟠镖客 2024-04-19 11:03 10 [回复]举报

重大火灾隐患判定方法GB35181-2017

5.1.3 下列情形不应判定为重大火灾隐患:

    a)依法进行了消防设计专家评审,并已采取相应技术措施的;
    b)单位、场所已停产停业或停止使用的;
    c)不足以导致重大、特别重大火灾事故或严重社会影响的。

梅有名 2024-04-23 10:35 00 [回复]举报

你是以什么身份来问这个问题?你如果不是消防管全责任人,你应该有个书面的东西,让消防安全责任人签字,虽然消防设施停用不需要向消防救援机构备案,但有明文规定要求消防安全责任人同意。