消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防联动控制器置于手动,打开干式供水测主排水阀,为什么报警阀不动作,压力开关和水力警铃动作

消防联动控制器置于手动,打开干式供水测主排水阀,为什么报警阀不动作,压力开关和水力警铃动作
独家星劫 | 2024-04-10 12:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

shawu 2024-04-13 17:13 00 [回复]举报

试警铃阀是从水源侧接出连接到报警管路,在报警管路出口处设自动滴水阀,从而不用干式报警阀组动作即可检验系统报警可靠与否的一个组件。除此之外想要系统报警只能是系统侧气压降低导致阀瓣打开,从而水流进入中间室再进入到报警管路,而单纯开启水源侧排水阀即不会使干式报警阀动作也不会使压力开关和水力警铃动作,否则就是阀组管路安装存在问题。

关闭

关闭

手机APP下载