消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

疏散通道上的防火卷帘与防火门同时设置,防火卷帘的控制逻辑?

设置在疏散通道上的特级防火卷帘,两侧都设置有专用温感,在防火卷帘旁设计有常开防火门。此时的防火卷帘,是否再需要设置两步降?

牧雪1984 | 2024-01-19 17:05
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

丶0427 2024-01-21 19:46 00 [回复]举报

需要

安洪全 2024-01-22 08:35 10 [回复]举报

疏散通道上的,需要设置两步降

火灾自动报警系统设计规范 GB50116-2013

4.6.3 疏散通道上设置的防火卷帘的联动控制设计,应符合下列规定:   

1 联动控制方式,防火分区内任两只独立的感烟火灾探测器或任一只专门用于联动防火卷帘的感烟火灾探测器的报警信号应联动控制防火卷帘下降至距楼板面1.8m处;任一只专门用于联动防火卷帘的感温火灾探测器的报警信号应联动控制防火卷帘下降到楼板面;在卷帘的任一侧距卷帘纵深0.5m~5m内应设置不少于2只专门用于联动防火卷帘的感温火灾探测器。

牧雪1984   回复: 安洪全2024-01-22 21:03

了解了解。之前项目上类似情况,最后专家是让把防火卷帘旁边的防火门的疏散指示取消掉了,不作为疏散通道。

0    0 [回复]举报

王宇晗   回复: 牧雪19842025-02-17 16:54

首先得确认该处防火门是否需要借用另一防火分区进行疏散,如果本防火分区满足疏散要求,则该防火门只作用于防火分隔,上方安全出口灯就需要去除

0    0 [回复]举报

关闭

关闭

手机APP下载