消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

如下图所示的一类高层住宅建筑,A户与B户间距1.8m,墙面缺口位置为窗户,请问开窗位置有什么防火要求呢?

innerpeace | 2024-01-04 11:46
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

阳明心 2024-01-04 15:39 00 [回复]举报

6.5.2 设置在防火墙、防火隔墙上的防火窗,应采用不可开启的窗扇或具有火灾时能自行关闭的功能。

马马马 2024-01-04 20:39 00 [回复]举报

窗扇应采用a级材质吧

同同不同 2024-01-06 07:15 00 [回复]举报

建规对住宅建筑相邻户开口之间的实体墙不小于1m,但图示仅提现了水平相邻洞口,未体现正对洞口,若距离过近应采取防止火灾水平蔓延的措施,比如砌筑凸出的分户墙

大白o 2024-01-29 11:39 00 [回复]举报

如为不同防火分区,可参考《建筑设计防火规范》GB50016-2014(2018年版)5.2.2条注1,;还需参考防火图示18J811-1中5.2.2图示图示10。

关闭

关闭

手机APP下载