根据规范要求,养老服务机构应该使用封闭式楼梯间。在实际生活中,养老服务机构,特别是乡镇养老院,普遍是普通型楼梯间或者是敞开式楼梯间。像这种情况该如何整改呢?

唐璋朋 | 2023-09-21 09:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

陈曲 2023-09-21 13:00 00 [回复]举报

既有建筑不涉及到重大调整或者专门的文件指示 其他看经济情况和心情

安洪全 2023-09-21 13:17 00 [回复]举报

两个思路,一个是加装防火门,变成封闭楼梯间(或防烟楼梯间),另一个是把过道变成敞开式外廊。

周家斌 2023-09-21 13:33 10 [回复]举报

乡镇养老院大多是有敞开式外廊与楼梯间想通的,可以不需要封闭楼梯间

永锅 2023-09-21 16:51 00 [回复]举报

老年人照料设施层数不超过5层,建筑高度不大于24m,疏散楼梯与敞开式外廊直接连通,可采用敞开楼梯间。


ant 2023-09-22 10:39 00 [回复]举报

5.5.13A 老年人照料设施的疏散楼梯或疏散楼梯间宜与敞开式外廊直接连通,不能与敞开式外廊直接连通的室内疏散楼梯应采用封闭楼梯间。建筑高度大于24m的老年人照料设施,其室内疏散楼梯应采用防烟楼梯间。
建筑高度大于32m的老年人照料设施,宜在32m以上部分增设能连通老年人居室和公共活动场所的连廊,各层连廊应直接与疏散楼梯、安全出口或室外避难场地连通。