装设网格、栅板类通透性吊顶的场所,当通透面积占吊顶总面积的比例小于70%时,喷头应设置在吊顶上方还是下方,还是上下都设?

永锅 | 2023-04-11 17:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

张牙舞爪的张 2023-04-12 13:44 00 [回复]举报

小于等于70%上下都设。

消防老胡 2023-04-12 17:39 00 [回复]举报

小于70%,喷头设置在吊顶下方(直立型)。上下都设一般有三种情形:《喷规》7.2.3 当梁、通风管道、成排布置的管道、桥架等障碍物的宽度大于1.2m时,其下方应增设喷头(图7.2.3);采用早期抑制快速响应喷头和特殊应用喷头的场所,当障碍物宽度大于0.6m时,其下方应增设喷头。以及《汽车库、修车库、停车场设计防火规范 GB50067-2014》7.2.6 设置在汽车库、修车库内的自动喷水灭火系统,其设计除应符合现行国家标准《自动喷水灭火系统设计规范》GB 50084的有关规定外,喷头布置还应符合下列规定: 1 应设置在汽车库停车位的上方或侧上方,对于机械式汽车库,尚应按停车的载车板分层布置,且应在喷头的上方设置集热板;还有就是《喷规》7.1.9 货架内置洒水喷头宜与顶板下洒水喷头交错布置,其溅水盘与上方层板的距离应符合本规范第7.1.6条的规定,与其下部储物顶面的垂直距离不应小于150mm。