喷淋头安装

配电柜上方能不能安装喷淋头
强周 | 2020-11-15 13:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

刘丽波 2020-11-16 09:23 10 [回复]举报

防护等级Ip55及以上等级可以。Ip30不可以。可以参考消水规11.0.9

黄辉   回复: 林@@2020-11-17 09:54

给您把链接加上:11 控制与操作

11.0.9 消防水泵控制柜设置在专用消防水泵控制室时,其防护等级不应低于IP30;与消防水泵设置在同一空间时,其防护等级不应低于IP55。

0    0 [回复]举报

周家斌 2022-05-09 10:21 10 [回复]举报

配电房使用细水雾喷头是可以的,

李勤 2025-06-13 16:05 00 [回复]举报

看下部柜子IP防护等级