消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

水泵接合器设置

水泵接合器有没有强制规定距建筑物外墙5米

范_vaGE | 2023-02-08 17:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

周家斌 2023-02-08 21:11 10 [回复]举报

没有强制性规定。水泵接合器应设在室外便于消防车使用的地点,临时高压消防给水系统向多栋建筑供水时,消防水泵接合器应在每座建筑附近就近设置,高层建筑一般设置在登高操作场地一侧。

张牙舞爪的张 2023-02-08 22:38 00 [回复]举报

《大型商业综合体消防安全管理规则》三十一条距离道路3米;《人员密集消防安全管理》7.6.9距离道路2米……建议看看有没有相关行业管理标准。室外、市政消火栓有5距离要求。

消防黄河 2023-02-09 08:33 00 [回复]举报

没有。设置在建筑外墙上也是允许的,原则是便于操作和确保使用安全。符合水规相关要求即可。

消防网友48128 2023-02-09 08:46 20 [回复]举报

没有,不应设玻璃幕墙下方,2米范围内无门窗洞口。

mshm 2023-02-10 09:21 20 [回复]举报

建筑设计防火规范8.1.11条文解释中讲到,外墙幕墙,装饰构件等火灾时易脱落,为消防员安全考虑。此类建筑规定水泵接合器距外墙不下于5米。

关闭

关闭

手机APP下载