消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防控制室设置问题

某公司中控大厅面积大约1200平方米,能否在大厅内设置消防控制室?注:消防控制系统与大厅生产plc控制系统都在大厅,有0.5米的距离,未分隔

执一不失 | 2023-02-06 12:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友48128 2023-02-06 21:23 00 [回复]举报

消防控制室不宜共用,宜靠外墙设置,2h+乙级防火门分隔,出口应直通室外或安全出口

张牙舞爪的张 2023-02-07 08:10 00 [回复]举报

只规定不能设置在强电设备间内或附近,房间要求参照设备房建设要求。

消防黄河 2023-02-07 18:06 10 [回复]举报

可以。如:石油化工企业设计防火标准:全厂性消防控制中心宜设置在中央控制室或生产调度中心,宜配置可显示全厂消防报警平面图的终端。等。

关闭

关闭

手机APP下载