消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

求教:一层和四层办公区域、生产区域公用一套预喷淋系统?

求教:一层和四层办公区域、生产区域公用一套预喷淋系统?有什么规范要求吗?

叶落 | 2022-11-16 11:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防网友68723 2022-11-19 10:20 00 [回复]举报

6.2.3 一个报警阀组控制的洒水喷头数应符合下列规定:       1 湿式系统、预作用系统不宜超过800只;干式系统不宜超过500只


6.2.4每个报警阀组供水的最高与最低位置洒水喷头,其高程差不宜大于50m。

关闭

关闭

手机APP下载