应急照明灯高度问题

对于消防应急照明灯安装高度问题,为啥只有最低高度要求而没有最高高度要求?

远古鱼龙 | 2022-06-13 13:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2022-06-13 14:57 00 [回复]举报

1、为了保证照明灯的光线能够有效覆盖疏散路径及相关区域的地面,照明灯宜采用顶部安装方式;受安装条件的限制,灯具也可以安装在疏散走道、通道两侧墙面或柱面上。由于距地面1m~2m的高度是人员的视线高度范围,为了避免照明灯的光线直接照射到人眼产生眩光,影响人员对疏散路径的识别,照明灯不能安装在距地面1m~2m的高度范围内。照明灯在墙面或柱面上安装时,可采用高位或低位两种安装方式:采用高位安装方式时,照明灯距地面的高度应大于2m;采用低位安装方式时,照明灯距地面的高度应小于1m,且应确保照明灯的光线直接照射到地面上。

2、高度也是有限制的,通过照度要求等于限制了灯具安装不是无限制的高。

远古鱼龙 2022-06-13 16:35 00 [回复]举报

谢谢!你太厉害了,得多向你学习请教。