多层少年宫是否设喷淋

一座建筑面积4000多平米,建筑高度23.4米的六层少年宫,空调设的VRv,是否需要设喷淋。

liuccso | 2021-09-17 11:05
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 7

sewenlook 2021-09-17 11:33 00 [回复]举报

要看少年宫里具体都是什么场所,多大面积。

liuccso   回复: sewenlook2021-09-17 14:44

面积6层4000平米,1~2层展示区,3~6层一些中小学生培训区吧

0    0 [回复]举报

一片冰雨   回复: liuccso2021-09-20 22:10

你这个最好是沟通一下辖区的城建消防审核验收人员怎么去看,这种条文没有明确规定的,要看辖区参谋如何把控。原来我在商场,厨房明文规定必须要做完整防火分隔,问题是那是一家火锅店啊,厨房里不动火,就一个煲汤的电磁炉。验收的时候,还是按厨房标准安装防火门、防火窗;后来,换了一个参谋,厨房里用电的没有明火的,防火分隔不够也过了,

0    0 [回复]举报

刘丽波 2021-09-17 12:50 00 [回复]举报

如设有集中送回风管道,需设置自喷系统。

liuccso   回复: 刘丽波2021-09-17 14:42

暖通就是VRv,没有集中送回风管道

0    0 [回复]举报

刘丽波   回复: liuccso2021-09-17 18:07

任一层面积大于1500或总面积大于3000平的展览建筑也需要设置自喷系统。

0    0 [回复]举报

LZH20211009 2021-10-09 11:25 00 [回复]举报

参考《建筑设计防火规范 GB50016-2014》(2018年版)需要设计喷淋,

8.3.4 除本规范另有规定和不适用水保护或灭火的场所外,下列单、多层民用建筑或场所应设置自动灭火系统,并宜采用自动喷水灭火系统:     

1 特等、甲等剧场,超过 1500 个座位的其他等级的剧场,超过 2000 个座位的会堂或礼堂,超过 3000 个座位的体育馆,超过 5000 人的体育场的室内人员休息室与器材间等;     

2 任一层建筑面积大于 1500m² 或总建筑面积大于 3000m² 的展览、商店、餐饮和旅馆建筑以及医院中同样建筑规模的病房楼、门诊楼和手术部;     

3 设置送回风道(管)的集中空气调节系统且总建筑面积大于 3000m² 的办公建筑等;     

4 藏书量超过 50 万册的图书馆;     

5 大、中型幼儿园,老年人照料设施;     

6 总建筑面积大于 500m² 的地下或半地下商店;     

7 设置在地下或半地下或地上四层及以上楼层的歌舞娱乐放映游艺场所(除游泳场所外),设置在首层、二层和三层且任一层建筑面积大于 300m² 的地上歌舞娱乐放映游艺场所(除游泳场所外)。