消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电间是否需要设置气体灭火系统

配电间是否需要设置气体灭火系统

在路上112 | 2025-06-12 09:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

李勤 2025-06-12 11:43 00 [回复]举报

喧哗 2025-06-12 14:02 00 [回复]举报

可以看一下建筑设计防火规范8.3.9的条文解释,高层建筑的配电室需要设置。

小唐12321 2025-06-12 15:05 00 [回复]举报

一般不需要

消防网友44950 2025-06-12 15:29 00 [回复]举报

8.3.9 下列场所应设置自动灭火系统,并宜采用气体灭火系统: GB50016-2014(2018)  版 

     8 其他特殊重要设备室。

  因此,这个需不需要设置气体灭火系统的看当地住建部门验收时人家提不提这个问题。一般原则是要设置气体灭火系统的

EHS专家-DL 2025-06-12 17:28 00 [回复]举报

分情况。

高层民用建筑的配电间‌,因火灾风险高且影响范围大,‌必须设置气体灭火系统‌(如七氟丙烷、全氟己酮)。依据‌:《建筑防火通用规范》GB55037-2022 将高层配电间列为“特殊重要设备室”,要求配置自动灭火设施。

多层/单层建筑的普通配电间‌ 非特殊重要设备、无人值守且仅服务于局部区域的配电间,‌可不设气体灭火系统‌,但需配置灭火器(ABC干粉型)。

牛丫头消防课堂 2025-06-13 00:37 00 [回复]举报

第一,看你是独立设置的配电室还是设置在其他建筑内的配电室;

如果是独立的配电室,需要依据《火力发电厂与变电站设计防火标准》 GB50229-2019

11.5.4 单台容量为125MV·A及以上的油浸变压器、200Mvar及以上的油浸电抗器应设置水喷雾灭火系统或其他固定式灭火装置。其他带油电气设备,宜配置干粉灭火器。
    地下变电站的油浸变压器、油浸电抗器,宜采用固定式灭火系统。在室外专用贮存场地贮存作为备用的油浸变压器、油浸电抗器,可不设置火灾自动报警系统和固定式灭火系统。


如果设置在其他建筑内,其它场所均设置灭火系统的情况下,配电室也应设置自动灭火设施,例如气体灭火系统、高压细水雾灭火系统、干粉灭火系统等。设置条件看《建筑设计防火规范》

潘天坤 2025-06-13 07:55 00 [回复]举报

一般认为附属在高层民用建筑内(非独立建造的)的配电室属于特殊重要设备室,应设置自动灭火系统,并宜采用气体灭火系统

其他建筑的配电室可以参照执行,不做强制要求,不过有时候设计单位认为一些区域比较重要也会设置自动灭火系统


建规GB50016条文说明提及:高层民用建筑内火灾危险性大,发生火灾后对生产、生活产生严重影响的配电室等,也属于特殊重要设备室


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准




关闭

关闭

手机APP下载