消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防供配电

教材上:当建筑物由一路35K V、 10K V或10K V电源供电时,二级负荷可由两台变压器各引一路低压回路在负荷端配电箱处切换供电。建筑设计防火规范GB 50016 -2014(2018版)10.1.4(3)将这条定为三级负荷

渔夫119 | 2025-03-27 14:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

小唐12321 2025-03-27 14:45 00 [回复]举报

10.1.3 除本规范第10.1.1条和第10.1.2条外的建筑物、储罐(区)和堆场等的消防用电,可按三级负荷供电。

10.1.4 消防用电按一、二级负荷供电的建筑,当采用自备发电设备作备用电源时,自备发电设备应设置自动和手动启动装置。当采用自动启动方式时,应能保证在30s内供电。

渔夫119 2025-03-27 15:20 00 [回复]举报

就是说由两台变压器的低压端各引一路至消防供电,这个现在是三级供电

关闭

关闭

手机APP下载