单独的消火栓泵房需要做应急照明吗

QQ君 | 2025-03-21 14:18
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

重庆消防 2025-03-21 14:48 00 [回复]举报

需要,同时也需要备用照明。

QQ君   回复: 重庆消防2025-04-01 16:18

单独的消火栓水泵房的需要应急照明,那应急照明配电箱可以放在水泵房吗?

0    0 [回复]举报

EHS专家-DL 2025-03-21 14:56 00 [回复]举报

独立的消火栓泵房需设置应急照明。根据《建筑防火通用规范》GB55037-2022第10.1.11条,‌消防水泵房属于火灾时仍需正常工作的消防设备房,必须设置备用照明‌,且作业面最低照度不应低于正常照明‌。

潘天坤 2025-03-21 15:00 00 [回复]举报

发生火灾时仍需工作、值守的消防水泵房应同时设置疏散照明和疏散指示标志