消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

锅炉房、油浸变压器等设置在建筑内时能与人员密集场所贴邻吗

建筑防火通用规范 GB55037-2022  4.1.4燃油或燃气锅炉、可燃油油浸变压器、充有可燃油的高压电容器和多油开关、柴油发电机房等附设在建筑内时应符合下列规定:
    1 当位于人员密集的场所的上一层、下一层或贴邻时,应采取防止设备用房的爆炸作用危及上一层、下一层或相邻场所的措施

而条文解释中写着“当受条件限制需与其他建筑贴邻时,需视贴邻部位的具体情况和这些设备房的实际火灾和爆炸危险性采用抗爆墙、防爆墙或防火墙分隔,并应避开会议室、多功能厅、餐厅、营业厅、教室等人员聚集的场所;当受条件限制需布置在建筑内时,应按本条要求采取相应的防火措施,且不允许设置在建筑中人员聚集的场所的上面、下面或贴邻。”


席晓贺 | 2025-03-04 11:33
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

jinyanwu 2025-03-04 17:17 00 [回复]举报

个人意见,仅供参考:

条文意思已经很明显了,不能

关闭

关闭

手机APP下载