风管与风机不能直接用防火帆布软连接吗?

各位老师,请问风管与风机不能直接用防火帆布软连接吗?

玉米_amTC | 2024-12-06 18:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

四川0826 2024-12-06 20:16 10 [回复]举报

用于防排烟系统不可以用软连接

云中飞翔 2024-12-06 20:43 10 [回复]举报

GB51251-2017《建筑防烟排烟系统技术标准》第6.3.4条第4款:风管与风机的连接宜采用法兰连接,或采用不燃材料的柔性短管连接。当风机仅用于防烟、排烟时,不宜采用柔性连接。

潘天坤 2024-12-06 21:45 10 [回复]举报

排烟系统及机械加压送风系统作为独立系统时,风机与风管应采用直接连接,现场不应加设柔性短管,不应设置减振装置