消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外消火栓需要设置减压吗?

建筑室外消火栓与室内消火栓共用消火栓消防水泵及管网,现在室外消火栓启泵动压测试压力是0.60Mpa,室外消火栓栓口需要设置减压吗?

早上回来 | 2024-12-04 09:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

jinyanwu 2024-12-04 09:48 00 [回复]举报

个人意见,仅供参考:

看设计,应该不需要,室内栓栓口有0.5Mpa动压限制,室外没有。

云中飞翔 2024-12-04 11:47 00 [回复]举报

室外消火栓的设计承压能力是有限的,当水源压力超过其承受能力时,可能导致消火栓接口漏水、阀门损坏,甚至整个消火栓爆裂。根据《消防给水及消火栓系统技术规范》7.4.12的要求,消火栓栓口动压力不应大于0.50MPa,当动压力大于0.70MPa时必须设置减压装置‌。

HOHO设计师 2024-12-04 13:07 00 [回复]举报

室外火栓通常不需要设置减压装置。不过,在某些特殊情况下,如果室外消火栓的出水压力过高,超过了消防设备或管道的安全工作压力,可能会考虑采取适当的减压措施。但是这种情况较为少见,一般情况下室外消火栓系统的设计会避免出现过高的压力。


你可以找个微信小程叫 ai规范

wetom 2024-12-04 17:04 10 [回复]举报

泵的扬程就限制了,不用减了。

关闭

关闭

手机APP下载