消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

灭火器配置计算

  如题,自学中,但是根据GB50140中计算灭火器的配置时,有疑惑,计算最小需配灭火级别:公式Q=KxS/U,这个公式中他们的取值有表格对照,下一步中,计算每个设置点的最小需配灭火级别:公式Qe=Q/N,这个N是如何取值的?怎么计算得来?

  再者,规范中,计算到这就结束了,只是计算出灭火级别了,还没计算出到底是配几具灭火器啊?咋弄

卫国 | 2024-11-13 11:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

strongcar 2024-11-13 14:11 10 [回复]举报

这个N是指保护区内设置几个灭火器的配置点,一般根据灭火器的最大保护距离来确定,只要不超过这个距离就行

缱绻一夏 2024-11-13 15:28 10 [回复]举报

N可以参考下表根据灭火器的最大保护距离,配置场所均匀覆盖上需要多少个点就是N,然后再Q/N算出来的就是单个点的最小配置级别

jinyanwu 2024-11-13 16:29 00 [回复]举报

比如说一个计算单元面积大约是50*50m,轻危险级,A类火灾,使用1A灭火器,单位保护面积是100,通过计算,需要25具1A灭火器即可,2500/100=25A/1A=25具,也就是说这个场所最小配备1A灭火器25具即可。但实际上还有个最大保护距离是25米,你在50*50方框内画半径为25米的圆,完全覆盖需要几个圆?那么就是几组灭火器,所以这个单元至少应该是4组。平均每组6.25具,超过了每个配置点不超过5具的规定,那就用25/5=5,所以需要设置至少5个配置点,每个配置点不超过5具,不少于2具即可。

当然这个是按照K=1,也就是现场没有消火栓和灭火系统;

同时现场单元不一定都是正方形的,这就要根据情况画圆确定多少组。

这个N就是根据保护距离和保护面积综合计算得到的。这个例子中N≥5即可。

如果是歌舞娱乐场所,配备的有消火栓和自喷系统,那就是严重危险级,3A灭火器,单位保护面积为50,计算=1.3*0.5*2500/50=32.5A,32.5/3A≈11具,最大保护距离为15m,如果画圆确定需要设置六个放置点,那么每个放置点至少需要2具,也就是共12具。但计算出来一般就是最少11具即可。考试时候配置点数量一般都会告诉你。现实中需要自己进行计算确定。

Dopp 2024-11-14 18:39 00 [回复]举报

根据


根据该场所的火灾危险等级,定是ABC哪类,然后选择对应的单具灭火器配置灭火级别,N=Q/Qe,算出该计算单元需要多少具灭火器,根据规范,单个计算单元不能少于两具,单处最多不能超过5具,一般按单处配置2具算,配置多少处=N/2

关闭

关闭

手机APP下载