各位老师,这个喷头需要装挡水板么?有依据没?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

阿龙 24-09-20

根据《自动喷水灭火系统设计规范》(GB50084-2017)第7.1.10条挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿宜与洒水喷头的溅水盘平齐。除下列情况和相关规范另有规定外,其他场所或部位不应采用挡水板: 1 设置货架内置洒水喷头的仓库,当货架内置洒水喷头上方有孔洞、缝隙时,可在洒水喷头的上方设置挡水板;2 宽度大于本规范第7.2.3条规定的障碍物,增设的洒水喷头上方有孔洞、 缝隙时,可在洒水喷头的上方设置挡水板。

根据图片内容,喷头上方有孔洞,可以加挡水板让喷头响应更快。

1 0 [回复]举报

磊中 24-09-24

这个喷头上面还有喷头吗?应该没有啊,你这个喷头本来就在吊顶上面吧,那肯定是不用的;

7.1.13 装设网格、栅板类通透性吊顶的场所,当通透面积占吊顶总面积的比例大于70%时,喷头应设置在吊顶上方,并符合下列规定:       1 通透性吊顶开口部位的净宽度不应小于10mm ,且开口部位的厚度不应大于开口的最小宽度;

另外,挡水板的作用1,不让喷头上方的水淋到,这样才能起到爆破喷水的效果2、让烟气聚集,温度达到好爆破喷头喷水,

0 0 [回复]举报

云中飞翔 25-01-09

镂空吊顶上方属于梁下安装,应为直立式安装,现场图片明显是下垂型安装,溅水盘距顶板高度应该超过了规范要求。另外,17版喷规明确严禁乱用挡水板作为集热装置。

0 0 [回复]举报