储烟仓高度大于500,与最小清晰高度大于1.6+0.1H有冲突怎么办?

储烟仓高度大于500,与最小清晰高度大于1.6+0.1H有冲突怎么办?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

香.香 24-05-31

储烟仓厚度与最小清晰高度有冲突是指什么冲突。储烟仓的厚度与房间净空高和采用的排烟方式有关系。自然排烟不小于净空高20%且不小于500mm.机械10%且500mm。走道、房间的最小清晰高度与它的净空高有关系,当不大于3米时,最小清晰高度不小于净高的1/2,若是其它区域的话才是你说的那个不小于1.6+0.1H。举个例子3米的走道、房间,自然排烟时储烟仓的厚度最小为0.6米,最小清晰高度为1.5米。0.6+1.5=2.1米有什么冲突呢?若是机械排烟则为0.5+1.5=2米。其它不大于3米的区域计算也是如此,自然时储烟仓厚度0.6米,最小清晰高度1.6+0.3=1.9米。机械时储烟仓厚度0.5米,最小清晰高度1.6+0.3=1.9米。怎么算也不觉得冲突。

0 0 [回复]举报

我头发贼黑 24-05-31

4.6.9 走道、室内空间净高不大于3m的区域,其最小清晰高度不宜小于其净高的1/2,其他区域的最小清晰高度应按下式计算:Hq =1.6 +0.1·H ′ 

0 0 [回复]举报

南明离火 24-06-01

净高如果只有2.2米呢

0 0 [回复]举报

黄-江西省景德镇市   回复: 南明离火24-06-01

净高2.2米,最小清晰高度1.1米,自然排烟储烟仓500mm,机械排烟储烟仓厚度也是500mm。规范对储烟仓的最低要求是≥500mm。

1 0 [回复]举报

潘天坤 24-06-03

走道、室内空间净高不大于3米的区域,其最小清晰高度不宜小于其净高的1/2;

其他区域(除走道、室内空间净高不大于3米的区域外)的最小清晰高度应按下式计算:Hq =1.6 +0.1·H ′ ;

当采用自然排烟方式时,储烟仓的厚度不应小于空间净高的20%,且不应小于500mm;

当采用机械排烟方式时,储烟仓的厚度不应小于空间净高的10%,且不应小于500mm;

挡烟垂壁、结构梁及隔墙等都可以作为防烟分隔的设施,所以同时设置挡烟垂壁、结构梁的区域,储烟仓的厚度=结构梁高度+挡烟垂壁高度。

不太理解楼主说的冲突是什么意思,请具体举个冲突的例子?

0 0 [回复]举报

阳明心 24-08-23

谢谢老师们解答,不冲突了

0 0 [回复]举报