消防问答 > 防烟排烟 提问

防排烟机房要不要配置自喷或消火栓以及灭火器?哪条规范?

防排烟机房要不要配置自喷或消火栓以及灭火器?哪条规范?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

灭邪斩 24-04-26

建筑防烟排烟系统技术标准 GB51251-2017

4.4.5 排烟风机应设置在专用机房内,并应符合本标准第3.3.5条第5款的规定,且风机两侧应有600mm以上的空间。对于排烟系统与通风空气调节系统共用的系统,其排烟风机与排风风机的合用机房应符合下列规定:
    1 机房内应设置自动喷水灭火系统;

0 0 [回复]举报

消防网友68723 24-04-28

烟规4.4.5 排烟风机应设置在专用机房内,并应符合本标准第3.3.5条第5款的规定,且风机两侧应有600mm以上的空间。对于排烟系统与通风空气调节系统共用的系统,其排烟风机与排风风机的合用机房应符合下列规定:
    1 机房内应设置自动喷水灭火系统;
    2 机房内不得设置用于机械加压送风的风机与管道;
    3 排烟风机与排烟管道的连接部件应能在280℃时连续30min保证其结构完整性。

0 0 [回复]举报

阳明心 24-04-28

当排烟风机与排风机合用一个机房的应设自喷,或一台风机平时排风火灾时排烟的机房也应设自喷。

0 0 [回复]举报

易学   回复: 阳明心24-04-29

不合用而独立的防排烟机房要不要设,有没有哪条规范要求?

0 0 [回复]举报

香.香 24-05-10

排烟系统与通风空气调节系统合用的时候应设置自喷。建筑防排烟系统技术标准GB51252-2017

0 0 [回复]举报

潘天坤 24-06-17

排烟系统与通风空气调节系统共用的系统的合用机房,机房内应设置自动喷水灭火系统,常见地下室汽车库区域。

当风机仅用于排烟系统时,机房内无需设置自动喷水灭火系统,但是一般会考虑灭火器配置(规范依据可以参考灭火器设置),常见屋面风机房。

风机房无需设置消火栓。

设置在屋面的加压送风机房一般没有设置自动喷水灭火系统。

设置在地下室或者楼层里的加压送风机房一般会设置自动喷水灭火系统。

0 0 [回复]举报

最新问题

关闭

关闭