消防问答 > 防烟排烟 提问

关于防排烟管道材料和做法是否满足规范耐火极限

目前防排烟管道按照规范要求设计1.5mm厚镀锌钢板➕50mm离心玻璃棉包覆的排烟管道,现对其耐火极限要求是否符合规范1小时提出质疑,是否能通过消防验收。请有关专业人士予以回复,感激不尽!

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

浴火重生 23-02-11

质疑的人很专业啊,包覆材料达到1.0h耐火极限,其熔点必须高于945摄氏度,必须使用厚度35㎜以上岩棉,或耐火800度以上的材料。

0 0 [回复]举报

消防网友78337 23-02-11

按照15K606图集中P159做法应该是最标准的


玻璃棉包覆只见13J811-1中建筑设计防火规范图集中,风管穿过防火墙体时进行防火保护。

0 0 [回复]举报

刘丽波 23-02-11

耐火极限包括耐火隔热性与耐火完整性,现场的包裹满足隔热性要求,完整性是否能满足?耐火极限由谁测定?如果是工业一体化生产的,就会有检测报告,是否满足规范要求很容易检测。

0 0 [回复]举报

潘天坤 24-06-24

离心玻璃棉材质燃烧性能可能达不到A级

同时隔热层材质密度是多少也有影响

最后就是是否能够提供通风管道耐火极限报告

近期有个项目复合风管送检耐火极限试验,材质大概是彩钢板+40毫米防火岩棉(密度110kg/m³)+1毫米镀锌钢板,最后结果大概能满足1小时耐火极限

0 0 [回复]举报

最新问题

关闭

关闭