地下商业B3是车库,B2是商场,B3和B2连接处是人行电梯及电动玻璃门,请问老师这样符合要求吗?谢谢

各位老师,地下商业B3是车库,B2是商场,B3和B2连接处是人行电梯及电动玻璃门,请问老师这样符合要求吗?谢谢

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 7 回答

许景程 24-11-26

按规范不可以。GB50016-2014建筑设计防火规范5.5.6 直通建筑内附设汽车库的电梯,应在汽车库部分设置电梯候梯厅,并应采用耐火极限不低于2.00h的防火隔墙和乙级防火门与汽车库分隔。

0 0 [回复]举报

阿龙 24-11-27

这种地方一般在扶梯上方走道会设置卷帘门进行分隔,设置了卷帘门就没有问题

1 0 [回复]举报

jinyanwu 24-11-27

这里应该不属于疏散区域,所以火灾情况下应该有一个防火卷帘门联动下降到地面;

同时下电梯这里门内外上部是不是连通的(吊顶区域),如果连通也不符合要求;

0 0 [回复]举报

红门铠甲   回复: jinyanwu24-11-28

老师好!有没有可能他们在同一防火分区


0 0 [回复]举报

jinyanwu   回复: 红门铠甲24-11-29

同一个防火分区也需要避免火灾或烟蔓延的措施,对于上下贯通的这种结构,往往限制条件还比较苛刻;并且一般这个自动步梯不作为疏散通道使用;你这个都到B2、B3层了,说明商场规模还不小,应该不可能会将上下两层作为一个防火分区对待,成本会非常高。

同时防火分隔往往跟随着防烟分隔。

当然还有一种可能,就是这个步梯上面一层四周都有防火卷帘,并且和上一层不连通,能够完全分隔,那么下面这个电动门就没有影响了。只是作为一个日常通行措施使用。

1 0 [回复]举报

红门铠甲   回复: jinyanwu24-12-02

感谢老师的透彻全面的分析,这样就比较容易搞懂了。

0 0 [回复]举报

红门铠甲   回复: jinyanwu24-12-03

感谢老师的回复解答,去实地查看了,他B2是开放式下沉式广场,等同于露天广场,这样的共计是符合规范要求的

0 0 [回复]举报