自喷喷头挡水板面积及尺寸要求

《自动喷水灭火系统设计规范》 GB50084-2017

7.1.10 挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿宜与洒水喷头的溅水盘平齐。除下列情况和相关规范另有规定外,其他场所或部位不应采用挡水板:      

    1 设置货架内置洒水喷头的仓库,当货架内置洒水喷头上方有孔洞、缝隙时,可在洒水喷头的上方设置挡水板;      

    2 宽度大于本规范第7.2.3条规定的障碍物,增设的洒水喷头上方有孔洞、 缝隙时,可在洒水喷头的上方设置挡水板。