消防水泵控制柜的防护等级要求

消防设施通用规范 GB55036-2022

 

3.0.12 消防水泵控制柜应位于消防水泵控制室或消防水泵房内,其性能应符合下列规定:    

    消防水泵控制柜位于消防水泵控制室内时,其防护等级不应低于IP30;位于消防水泵房内时,其防护等级不应低于IP55

 

    消防水泵控制柜是保证消防给水系统可靠运行的关键部件,在准工作状态下的防水、防尘等性能和在火灾状态下的启动性能必须得到保障,避免贻误因灭火时机而影响火灾扑救效果,甚至失败。

 

消防给水及消火栓系统技术规范 GB50974-2014

 

11.0.9 消防水泵控制柜设置在专用消防水泵控制室时,其防护等级不应低于IP30;与消防水泵设置在同一空间时,其防护等级不应低于IP55。

    消防水泵房内有压水管道多,一旦因压力过高如水锤等原因而泄漏,当喷泄到消防水泵控制柜时有可能影响控制柜的运行,导致供水可靠性降低,因此要求控制柜的防护等级不应低于IP55,IP55是防尘防射水。当控制柜设置在专用的控制室,根据国家现行标准,控制室不允许有管道穿越,因此消防水泵控制柜的防护等级可适当降低,IP30能满足防尘要求