厂外道路路边是指机动车道的边缘还是人行道的边缘?

建规3.5.1,甲类仓库到厂外道路路边的防火间距为20米。现在一个项目甲类仓库(存放一桶乙醇),距离厂外机动车道的边缘21米,距离厂外人行道边缘15米,是否符合?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

消防检查 24-07-19

我认为不符合,“距道路”应该包含人行道。

0 0 [回复]举报

LHH2737 24-07-19

指的是机动车道,3.5.1条的条文解释:甲类仓库与道路的防火间距,主要考虑道路的通行情况、汽车和拖拉机排气管飞火的影响等因素。一般汽车和拖拉机的排气管飞火距离远者为8m~10m,近者为3m~4m。考虑到车辆流量大且不便管理等因素,与厂外道路的间距要求较厂内道路要大些。

1 0 [回复]举报

周家斌 24-07-19

人行道也是道路,15米是不满足要求的

1 0 [回复]举报

phone0224 24-07-19

道路包括人行道的。

0 0 [回复]举报