消防问答 > 防烟排烟 提问

风管防火包裹的做法有没有具体规范要求

风管防火包裹的做法有没有具体的规范要求,还是说只要达到规范要求的耐火极限就可以了?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

安洪全 24-06-18

图集会有推荐做法,或者是可靠的做法推荐。但原则上只要满足耐火极限就是可以的,只不过需要自证。

0 0 [回复]举报

最帅游客   回复: 安洪全24-06-18

谢谢

0 0 [回复]举报

潘天坤 24-06-18

做法应该满足耐火极限要求,同时要注意整体防火保护措施的材料均应该为A级燃烧性能

市面上常规做法为防火板+岩棉,很多图集也有相关做法

现场新材料很多,有各种各样的报告,隔热层比较薄和非常规做法可能要质疑报告的真实性

0 0 [回复]举报

冼锟 24-06-20

40mm防火岩棉+8mm防火板

0 0 [回复]举报