格栅下的喷头需要安装集热罩吗?

格栅吊顶安装的下喷头(现场为上下喷)需要安装集热罩吗,规范有要求吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 11 回答

周家斌 23-11-20

不是集热罩,是挡水板,挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡

1 1 [回复]举报

玺望成真   回复: 周家斌23-11-20

您好,但是规范里没有写格栅吊顶的下喷必须要按照挡水板啊。

0 0 [回复]举报

南明离火   回复: 周家斌23-11-20

我记得有见过一个说法,格栅不用加挡水板或集热罩,镂空更有利于喷头快速达到破裂温度

0 0 [回复]举报

周家斌   回复: 南明离火23-11-20

参考石老师资料:通透性吊顶场所-洒水喷头布置要求 https://b.1190119.com/article-235.htm?keywords=%e6%8c%a1%e6%b0%b4%e6%9d%bf

0 0 [回复]举报

玺望成真   回复: 南明离火23-11-21

镂空对喷头的破裂是不利的,因为温度都通过空隙到上面去了。

0 0 [回复]举报

安洪全 23-11-20

为啥不改成直立型喷头?

规范就没有集热罩的叫法,挡水板倒是有,避免周围喷头动作后水喷到后影响动作温度。

虽然成本低,但不可靠,能用于的地方,好像只有多层货架中喷头。

0 0 [回复]举报

玺望成真   回复: 安洪全23-11-21

有上喷,上下喷都有。

0 0 [回复]举报

安洪全   回复: 玺望成真23-11-21

其实下垂型喷头都可以取消,如果将来还有可能变回石膏板吊顶的话,就增加挡水板。

0 0 [回复]举报

资源网小助理 23-11-22

增加挡水板

0 0 [回复]举报

玺望成真   回复: 资源网小助理23-11-24

没有规范支撑啊。

0 0 [回复]举报

开了要关 23-12-14

关于挡水板边缘平齐

关于规范解释,挡水板边缘平齐溅水盘,这个能不能突破

0 0 [回复]举报