消防问答 > 消防给排水 提问

消防备用泵

消防给水环状供水,在满足消防给水及消火栓系统技术规范第5.1.10条时可不设置备用泵吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

充楞装傻 22-04-24

0 0 [回复]举报

消防网友78337 22-04-24

该条款没有条文说明,

个人认为,从严来说,不是说满应条件的消防水泵可不设置备用泵,只是消防备泵降低一点性能;



 如果从宽说,设计人员一定要省台备用泵。从5.1.10的条件,结合3.3.2和3.5.2条的要求,能省泵的建筑单体体量都非常小,如果你只建一个独立的3000平方左右的小建筑,只一台消防泵,也没什么。

一个整体,小区或建筑群,集中用泵,这个泵省不省,意义不大。

0 0 [回复]举报

最新问题

关闭

关闭