消防问答 > 自喷灭火系统 提问

请教大家一个问题:关于预作用采用的喷淋头的问题。

请教大家一个问题:去检测时候发现一车库预作用系统喷淋头设置在排烟管道下方,并且采用了普通下喷,按规范要求预作用系统应采用直立性洒水喷头或干式下垂型洒水喷头,指出后对方施工人员称:投标答疑时,风管下喷可采用普通下喷,请问这种说法是否成立?住建验收能通过吗,总感觉没有依据。

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

资源网小助理 25-06-27

即便采用了干式下垂型喷头,这个短立管还是会存水,需增加一个泄水阀,试水后逐一排空。


1 0 [回复]举报

牛丫头消防课堂 25-06-27

按规范要求,干式下垂型喷头。但是同时需要考虑泄水。

有些地区不查。我们山东淄博,查!

1 0 [回复]举报

李勤 25-06-30

规范要求采用干式下垂喷头,天津住建委验收时提过此类问题。

0 0 [回复]举报