消防问答 > 建筑防火 提问

食品冷藏冷冻库的防火间距、防火分区和疏散是按照通规标准还是按照冷库设计规范进行消防设计

通规要求两栋丙类仓库的防火间距是10米,防火分区面积是1200平米,冷库设计规范没有防火间距的规定,防火分区面积是3500平米的标准,通规要求300平以上丙类仓库两个安全出口,冷库设计规范没有列举疏散标准,冷库门是否可以作为疏散门?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


精彩评论

牛丫头消防课堂 25-06-27

冷库内部人员很少,规范没考虑冷库内部人员疏散。但是考虑人员紧急情况下呼救按钮。

7.3.9 冷藏间内宜在门口附近设置呼唤按钮,呼唤信息应传送到制冷机房控制室或有人值班的房间,并应在冷藏间外设有呼唤信号显示。设有呼唤信号按钮的冷藏间,应在冷藏间内门的上方设置常明灯。设有专用疏散门的冷藏间,应在冷藏间内疏散门的上方设置常明灯。

查看原文

共 4 回答

牛丫头消防课堂 25-06-27

冷库内部人员很少,规范没考虑冷库内部人员疏散。但是考虑人员紧急情况下呼救按钮。

7.3.9 冷藏间内宜在门口附近设置呼唤按钮,呼唤信息应传送到制冷机房控制室或有人值班的房间,并应在冷藏间外设有呼唤信号显示。设有呼唤信号按钮的冷藏间,应在冷藏间内门的上方设置常明灯。设有专用疏散门的冷藏间,应在冷藏间内疏散门的上方设置常明灯。

查看原文

罗马苏丹 25-06-25

你可以看看冷库设计标准GB50072,对冷库的防火间距、防火分区面积、疏散标准均有明确要求

0 0 [回复]举报

李勤 25-06-26

看冷库规范(有专业规范看专业规范,专业规范没有涉及的在通用的规范)

0 0 [回复]举报

潘天坤 25-06-26

疏散门有相关要求,是否可以作为疏散门要看是否满足疏散门要求


专业规范没有规定的,可以按照通用规范执行

0 0 [回复]举报

牛丫头消防课堂 25-06-27

冷库内部人员很少,规范没考虑冷库内部人员疏散。但是考虑人员紧急情况下呼救按钮。

7.3.9 冷藏间内宜在门口附近设置呼唤按钮,呼唤信息应传送到制冷机房控制室或有人值班的房间,并应在冷藏间外设有呼唤信号显示。设有呼唤信号按钮的冷藏间,应在冷藏间内门的上方设置常明灯。设有专用疏散门的冷藏间,应在冷藏间内疏散门的上方设置常明灯。

0 0 [回复]举报

最新问题

关闭

关闭