常闭式排烟口

常闭式排烟口必须要设置远程执行机构吗?规范有规定吗?谢谢

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

LD 25-06-20

依据《建筑防烟排烟系统技术标准 GB51251-2017》6.4.3 常闭送风口、排烟阀或排烟口的手动驱动装置应固定安装在明显可见、距楼地面1.3m~1.5m之间便于操作的位置,预埋套管不得有死弯及瘪陷,手动驱动装置操作应灵活。

1 0 [回复]举报

李勤 25-06-20

0 0 [回复]举报

牛丫头消防课堂 25-06-20

如果设置在高处的常闭排烟口应该设置手动操作机构,因为火灾时人员打开排烟口操作机构,应该要联动排烟风机启动,所以应在1.3—1.5米高度处设置操作机构。具体条款为《建筑防烟排烟系统技术标准》第6.4.3条。

0 0 [回复]举报

罗马苏丹 25-06-20

只要求必须有现场手动开启方式,未规定远程控制

0 0 [回复]举报

潘天坤 25-06-26

没有设置执行机构的话,排烟口就没办法常闭。市场上的排烟口一般是常开口,所以需要设置手动操作装置使其常闭



0 0 [回复]举报

好记性不如烂笔头 25-06-29

远控多页送风口能不能设置成近控的

0 0 [回复]举报