室外卸货区防火间距

物流中心项目,贴临二层交易办公楼外设置单层卸货区,卸货区有钢结构顶棚(与办公楼同高),除贴临侧外其余三面均开敞。这种卸货区需不需要按停车场的防火间距6m?如不需要的话,办公区开向卸货区的门窗是否要设置防火门窗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

EHS专家-DL 25-06-09

开敞式卸货区不属于封闭建筑,可不执行《建筑设计防火规范》(GB 50016)中关于建筑物之间的防火间距要求(如停车场6m间距)。

办公楼贴临侧门窗必须采用‌甲级防火门窗‌(耐火极限≥1.5h),并确保火灾时自动关闭。若卸货区涉及危化品运输或高频作业,个人建议在贴临界面增设‌宽度≥2m的防火挑檐‌,防止火焰蔓延。

0 0 [回复]举报

李勤 25-06-09

0 0 [回复]举报

牛丫头消防课堂 25-06-09

建议你看看《物流建筑设计规范》 GB51157-2016第15.3.8条: 当物流建筑之间设货物运输连廊时,连廊的一端应采取防止火灾在相邻建筑间蔓延的分隔措施。

如果存在多座多层或高层物流建筑由楼层货物运输通道连通,那就得符合以下规定

15.3.2 当多座多层或高层物流建筑由楼层货物运输通道连通时,其防火设计应符合下列规定:     1 每座物流建筑的占地面积、防火分区面积及防火间距应符合现行国家标准《建筑设计防火规范》GB 50016的规定;     2 每座建筑及楼层货物运输通道的耐火等级不应低于二级;通道的顶棚材料应采用不燃或难燃材料,其屋顶承重构件的耐火极限不应低于1.0h;     3 汽车通道两侧进行装卸作业时,通道的最小净宽不应小于30m;楼层货物运输通道仅作为车辆通行时,多层物流建筑之间不应小于10m,高层物流建筑之间不应小于13m;     4 每个防火分区应设2个安全出口,当在楼层货物运输通道上设置直通首层的疏散楼梯时,人员可以疏散到楼层货物运输通道;当通道两侧布置物流建筑时,通道上的任一点至直通首层的疏散楼梯的距离不应大于60m;     5 顶层的楼层货物运输通道向室外敞开面积不应小于该层通道面积的20%;其他楼层自然排烟面积不应小于该层通道面积的6%;当通道高度大于6m时,通道内与自然排烟口距离大于40m的区域,应设机械排烟设施;     6 楼层货物运输通道内应设置消火栓和自动灭火设施;     7 楼层货物运输通道应设应急照明和疏散指示标识。

0 0 [回复]举报