消防问答 > 安全疏散 提问

用气灭保护区疏散距离和防火分区面积不能按有喷淋计算?

有专家用气灭保护区疏散距离和防火分区面积不能按有喷淋计算,感觉不是很合理啊,气灭保护不算保护了?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

磨砂猴 25-05-30

气灭一般都是一个房间内,在喷气之前人就应该疏散出来,所以气灭对疏散没有任何的帮助,而喷淋在发生火灾后会很快的动作,人可能还没来得及疏散,喷淋会减缓火灾的发展,所以可以延长疏散距离。

0 0 [回复]举报

牛丫头消防课堂 25-05-30

这个说法依据在《建筑设计防火规范》 GB50016-2014(2018年版)第5.5.17表注3

3 建筑物内全部设置自动喷水灭火系统时,其安全疏散距离可按本表的规定增加25%

0 0 [回复]举报

李勤 25-05-30

建规5.5.17 注释4. 当该场所设置自动喷水灭火系统时,室内任一点至最近安全出口的安全疏散距离可分别增加25%。(说的是自动喷水,规范没有提到其他相关灭火设施。)


1.设置自动喷淋场所有效延缓火灾蔓延,(变相扩大了疏散可用时间)所以增加了相应的疏散距离

2.气体防护区只有30秒延时,就算有了灭火设施,没有增大人员疏散的时间,所以不能增大计算疏散距离

0 0 [回复]举报

小唐12321 25-06-03

不算,我没见过哪个规范说算。

0 0 [回复]举报

最新问题

关闭

关闭