直接式探火管灭火装置上这根短的探火管作用是什么?

直接式探火管灭火装置上这根短的探火管作用是什么?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

EHS专家-DL 25-03-26

是否也是触发元件吧。短管受热破裂,内部压力骤降,直接触发灭火剂钢瓶的机械式启动装置,实现无电源自启动‌。

0 0 [回复]举报

萨曼岛的工程师   回复: EHS专家-DL25-03-26

这个是在保护区外的,不是那根长的。

0 0 [回复]举报

EHS专家-DL   回复: 萨曼岛的工程师25-03-26

咨询了设备厂家,该小段探火管作用是用于启动容器阀的,起启动作用。

0 0 [回复]举报

EHS专家-DL   回复: 萨曼岛的工程师25-03-26

平衡压力作用,详见:https://zhuanlan.zhihu.com/p/69982321 

0 0 [回复]举报

萨曼岛的工程师   回复: EHS专家-DL25-03-27

为什么长的探火管不直接连接在容器阀上(这样也是探火管破裂,压力降低,也可以打开容器阀),而是需要通过一个三通阀,再通过一根短管连接容器阀?

0 0 [回复]举报

EHS专家-DL   回复: 萨曼岛的工程师25-03-27

我的理解是这样的,探火管承受压力相对灭火剂容器瓶内压力要稍小,因为容器阀内有个密封装置及弹簧机构顶置住密封机构,为使密封机构上部也有压力设置了该小段探火管。这段气体灭火装置容器阀3D剖视视频可能对我们理解有帮助,https://zhuanlan.zhihu.com/p/69982321

1 0 [回复]举报