消防问答 > 防烟排烟 提问

请教一下几位老师,正压送风口出口处是否应加装防火阀

请教一下几位老师,正压送风口出口处是否应加装防火阀,谢谢


请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

沙葱胡辣汤 24-12-14

电梯间前室、楼梯间前室、避难间、避难层正压送风机需要设防火阀。楼梯间送风口采用百叶送风口,不加防火阀。

1 0 [回复]举报

溜达呀 24-12-14

楼梯间的正压送风口就不需要防火阀,一般采用自垂百叶(常开)… 因为楼梯里间上下是连通的。楼梯间前室、电梯前室、避难间等正压送风口需要安装防火阀,有火情的话需要联动开启本楼层(或防火分区)和相邻上下层的防火阀。

1 0 [回复]举报

李中良 24-12-16

正压送风口出口处没有规定要求安装防火阀。楼梯间送风口常开,前室等送风口常闭,火灾时相应位置需联动打开,但不是用防火阀。

2 0 [回复]举报

清静一念 24-12-16

建筑设计防火规范 GB50016-2014(2018年版)11 通风、空气调节系统的风管在下列部位应设置公称动作温度为70℃的防火阀:
1 穿越防火分区处;
2 穿越通风、空气调节机房的房间隔墙和楼板处;
3 穿越重要或火灾危险性大的场所的房间隔墙和楼板处;
4 穿越防火分隔处的变形缝两侧;
5 竖向风管与每层水平风管交接处的水平管段上。
注:当建筑内每个防火分区的通风、空气调节系统均独立设置时,水平风管与竖向总管的交接处可不设置防火阀。

3.3.6 加压送风口的设置应符合下列规定:
    1 除直灌式加压送风方式外,楼梯间宜每隔2层〜3层设一个常开式百叶送风口;
    2 前室应每层设一个常闭式加压送风口,并应设手动开启装置;
    3 送风口的风速不宜大于7m/s;
    4 送风口不宜设置在被门挡住的部位

1 0 [回复]举报

最新问题

关闭

关闭